If anyone's got an NB20 type 2 (the really old ones) kicking around they could sell me kindly PM me.....Need one following a small job today (pond socket back to back with an inside socket). Recently refurbed house,lots of electrics done, NAPIT cert showing all tests, including as expected r1,rn and r2 results. Only when I tested I got open circuit on all 3. So much for NAPIT certs,toilet paper this particular one.
After much deliberation it was decided to reduce the present 30a mcb on the circuit to a 20a and see how it goes....might not be viable as the kitchen is on it along with most of the rest of the house,if there are problems then we'll look at splitting to two radials ,but client reluctant to spend any time/money on it.
After much deliberation it was decided to reduce the present 30a mcb on the circuit to a 20a and see how it goes....might not be viable as the kitchen is on it along with most of the rest of the house,if there are problems then we'll look at splitting to two radials ,but client reluctant to spend any time/money on it.