The X/R in relation to MCBs is rather misleading, it relates to the capacity to interrupt the current, basically there are two aspects - firstly it is easier to switch resistive loads rather than ones of lower power factor (hence you may see 15A resistive/7A reactive type rating on some switches), the second is on large sites where there are many motors or similar (hence high X) when a fault occurs these motors contribute to the fault at the very early stages, however later on they can't sustain it, so a site with many motors will have a sustained fault level equal to that of the supply, but within the first few ms it would be considerably more - just at the point when a MCB/MCCB would be opening on a magnetic/instantaneous fault.
The international standards IEC/EN take this into account within the specification for switches, circuit breakers etc such that it must operate at appropriate power factors, and motor contribution as standard - so the switch example above under IEC/EN/BSEN would be a 7A switch, even though physically it could actually work adequately for larger resistive current ratings.
At medium and high voltage however this needs to be accounted for.
In the US, they follow this practice on to LV and rate their breakers quite differently, in general they test at a power factor of 0.5 (lower at higher current ratings) and assign the rating based on that. Then there are correction factors that they apply (without test) to rate the breaker for other power factors.
So under IEC etc a breaker may be able to open 750A at power factors down to 0.2, it must be tested over this whole range up to 1.0 and show it works effectively.
This same breaker may be sold into the US where it has a rating of 1000A, and under US standards it must be tested at a power factor of 0.5.
Now if you need to use the IEC rated one over unusual ranges - big local motor contribution etc you merely check the effective power factor is within the rating and the job's done.
In the US you would actually use an effective X/R - this corresponds to our use of pf, so for the same example a pf of 0.2 actually would be X/R = 4.9 and using a look up table then say the 1000A breaker should be suitable for 762A as the correction factor for X/R = 4.9 is 0.762
I think the actual requirements are now changing in the US, I think new ANSI standards are changing this such that MCCB are going to be rated at 0.15pf (X/R = 6.6) which is more in line with IEC stuff.
It should be noted that the specification is different for each piece of kit, for example a domestic light switch is tested over a different duty cycle than say a motor starter contactor. As I said in my earlier post you would need to check the appropriate standard covering the item of switchgear to see what the test parameters are.