J

JAMES_PRIOR

Brand new boiler, pump, room stat, 3 port valve, cyl stat & programmer fitted. Boiler will only fire when cyl stat turned up and then you can control heating from room stat. when cyl stat turned down the boiler will not fire and heating or hot water cannot be controlled. When cyl stat turned down and you call for heat via the room stat the 3 port valve seems to tick as though the 230v feed is being switched on and off. All wiring has been checked 5 times now my head is ready to go bang!
 
Hi.

If you are 100% certain the wiring is correct, (Check Here) have you tested at the mid pos valve to ensure correct operation???

Also could it be that the HW OFF/ON is mixed at cylinder stat or the programmer???
 
Hi Lenny,
Thanks for taking the time to assist!
I re-wired the central heating system myself and have checked all of the connections at each of the stats pump & programmer twice over. I have rewired y plan systems before and have been an electrician for 10 years now but iam starting to doubt myself! Iam going to the job tomorrow to go over it again so just wondered if anyone had come across this problem before.
 
Is the programmer working corrctly?,as you have done y plans before you will already know about the need for hw on/hw off at the programmer and cylinder stat,is the cylinder stat working correctly?,did you use a honeywell circuit board wiring centre if so,did you cut the correct links?,i have found the h/well booklet useful when fault finding,step by step and a quick way to resolve any issues.
 
The programmer is brand new and i have tested the s/lines at the wiring centre to make sure correct sequence and switching is achieved and the same for the cylinder stat. I was reading somewhere else that it might be a faulty micro switch on the 3 port valve but that wouldnt explain the feed which is only there when the cyl stat is turned up. At the job tomorrow so will check the links again.

Thanks for the ideas guys much appreciated!
 
have you ensured the HW off wire has been connected its the white one one the valve, the three port valve are a very clever piece of engineering
 
Hi James
Quote 'a faulty micro switch on the 3 port valve'. This would seem a logical explanation, as others have said its a clever piece of kit. I've never delved into its internal workings or observed this particular fault, so I would be interested in the outcome.

My thoughts for tracing stubborn faults on systems using these valves are....Disconnect the orange, white and grey wires and then test for the appropriate inputs at the terminals where the wires were connected ( This being necessary because the internal switching operations cause back feeds) see this link Honeywell United Kingdom Heating Controls

The relevant bit is at the bottom of page 2
 
Last edited by a moderator:
have you ensured the HW off wire has been connected its the white one one the valve, the three port valve are a very clever piece of engineering

HW off on programmer/satisfied on cylinder thermostat is connected to the gray wire on the valve,white is connected to room thermostat /heating demand

The clicking on and off is often a problem with a faulty head

a easy ref site for heating system wiring

http://octaveblue.co.uk/c_heating/index.htm
 
Last edited by a moderator:
The hot water off wire is grey! not white! On a three port valve. The white is call from the heating. If you've checked all your wiring and are happy with the connections the only obvious cause is the valve, I work on all kinds of heating systems everyday and have done for several years, i would change the valve mate. if its not the valve its your wiring.
 

Reply to Y Plan Headache! in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

I have just looked at the wiring diagram on line and there are a lot of internal links which if in the wrong terminal could put 230 volt onto...
Replies
10
Views
662
S
  • Article
Electrician Boiler Fault Boiler Fault I’m hoping someone can help with this boiler problem. Couple have just moved into a house that has a Grant...
Replies
0
Views
182
S
I was thinking that when the new two port opens and turns boiler and pump on, the normally open port (priority) on the three port is uncontrolled.
Replies
12
Views
2K
Does this help, note com is out not in I have a extended version using this basic system.
Replies
9
Views
2K
T
  • Article
Indirect (Boiler Fed) Megaflo Doesn't Stop Heating Hi, I noticed yesterday that when my HW is on, that the boiler runs constantly... I even...
Replies
0
Views
146
techweb
T

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks