P

Penance

Been to look at a job today, initially adding 3 dso's to ring final.
Was checking the CU and yes there is no main bond to the incoming water.
The water enters a utility room thru a concrete floor, stop cock and around 2' of copper pipe before changing to plastic pushfit stuff.
The plastic runs for about 10' and reverts to copper.

You know what I'm going to ask!
Does the small length of incoming metal water pipe require bonding back to the MET?
 
I once had a disagreement with an NICEIC area engineer on a newish house that was entirely plastic including the water company's blue pipe. I had to retake some floor boards up to prove a point!! Then he just mumbled and moved on to some thing else
 
Difficult one here

This is the guidance on the subject

If the incoming pipes are made of plastic, but the
pipes within the electrical installation are made of
metal, the main bonding must be carried out. The
bonding being applied on the customer side of any
meter, main stopcock or insulating insert and of
course to the metal pipes of the installation.


If the incoming services are made of plastic and
the pipework within the building is of plastic then
no main bonding is required. If some of the
services are of metal and some are of plastic, then
those that are of metal must be main bonded.

The part I underlined may be applicable

You can test to see if its extraeneous
or take the advise that appears to say yes it does need man bonding
 
Des that's fairly much what I was looking at, does seem a bit vague.

Sorry, using phone to view forum and it's not showing anything underlined.

I will be checking the other pipe work to see if it is extrenuous, no mft at the mo but one on way before I commence any work.
 
I had a similar scenario recently. A supposedly all plastic installation. When i got back to the job, after some time away there was an abundance of copper. When i tested it for continuity between my main earth terminal it read >1999.
When i put my insulation resistance tester on it read 0.00MΩ so i ran a M.E.B to it. Luckily it was not to difficult to get one there
 
Spoke to chap this morning and he's agreed to having the bonding sorted along with the extra sockets, also added outside light and loft lights to the list, nice result.
 

Reply to Yes a bonding question! in the Talk Electrician area at ElectriciansForums.net

Similar Threads

  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
Replies
24
Views
1K
  • Question
4-5 hours for 150? no chance, this is 2024, 150 for 2 hours maybe, that said an hour seems pretty quick, not sure he did the job right
Replies
23
Views
2K
The power company only brings in 3 wires which is 2 live and 1 neutral wire. It’s our responsibility to add the ground rod to bond the neutral...
Replies
3
Views
539
  • Question
Ok. Thanks
Replies
6
Views
1K
  • Question
edit : It was Emma Shaw that got electrocuted, Lisa Shaw was killed off by the rona jab.
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks