A prospective customer has contacted me via a recommendation received from a mutual contact and asked me to provide a quotation for remedial works that have arisen from an EICR that was recently undertaken at a three-bedroom property he rents out. In his initial e-mail, he said that the letting agent has told him that the following remedial works are necessary:

Replace Fusebox then test and certify
Materials to replace a double socket
Materials to install main gas bond, 10m of 16mm earth cable, 2 bonding clamps

I asked the property owner to forward me a copy of the EICR. I have redacted all personal details contained therein and have uploaded the report for your consideration, scrutiny and appraisal. My own personal assessment is that the property owner has been ripped-off by a drive-by tester and that the report isn't worth the paper that it's written on. Although the property owner was charged just ÂŁ95.00 by the letting agent, even this amount could be considered excessive given the poor quality of the report.

Over to you guys .....
 

Attachments

  • EICR-edited.pdf
    309.8 KB · Views: 427
Last edited:
I have just done an EICR , I waved my note book at the consumer unit , poked my head round a few doors did i mention I left my tester in the van but no matter I know what the readings will be anyway.
I am going to scribble some notes on my test sheets , tick a few boxes at random as you do and head down the pub for lunch.
ÂŁ195 cash in my pocket for 45mins work.

Am I doing this right ???
Don't worry Dusty, you'll soon get faster with some experiance.
 
I have just done an EICR , I waved my note book at the consumer unit , poked my head round a few doors did i mention I left my tester in the van but no matter I know what the readings will be anyway.
I am going to scribble some notes on my test sheets , tick a few boxes at random as you do and head down the pub for lunch.
ÂŁ195 cash in my pocket for 45mins work.

Am I doing this right ???
No you should be doing it from your van.
 
4. Mandatory inspection and testing of private rented accommodation in Scotland takes place every five years, not three as is stated on the report.
Much of what you point out is valid, however I will have to disagree on this point. Regardless of whether the legal requirement is for these to be carried out five-yearly or not, the Report must surely state a recommendation to next inspection based upon the condition of the electrical installation. Otherwise the box would be pointless.

So if the condition of the installation warranted the advice of three years to the next inspection, then that is the interval that should be stated. Or if it was in really bad condition then perhaps six months or whatever. I have had this issue before with business owners complaining that I had not given a five year recommendation for their business premises. I pointed out that my assessment was based on the installation as inspected - as it is required to be.
 
Much of what you point out is valid, however I will have to disagree on this point. Regardless of whether the legal requirement is for these to be carried out five-yearly or not, the Report must surely state a recommendation to next inspection based upon the condition of the electrical installation. Otherwise the box would be pointless.

So if the condition of the installation warranted the advice of three years to the next inspection, then that is the interval that should be stated. Or if it was in really bad condition then perhaps six months or whatever. I have had this issue before with business owners complaining that I had not given a five year recommendation for their business premises. I pointed out that my assessment was based on the installation as inspected - as it is required to be.

I understand and would not normally take issue with what you say. However, in this particular instance I seriously doubt that an installation which the tester has assessed as being only 15 years old would require periodic testing at three-year intervals. Fifty years, perhaps, yes. Fifteen, no. Not unless the installation was in unusually poor condition for its age. But in the absence of any test results we have no way of determining if this is actually the case here.
 
According to a landlord customer of mine ÂŁ65. Can I beat that price she has been quoted ? :laughing:

Yes of course madam , and I will drive past tonight and compile my report this evening. I won’t even have to disturb the tenants.
It will be with you via email at 9am tomorrow morning

Please deposit ÂŁ64 into this bank account
 
I've just quoted a private landlord ÂŁ250, it's a 3 bed house. I always explain that I have to be thorough as it's important and need a day to do it right including the paperwork. Accepted immediately. :) But in that price we'd replace the odd damaged socket or light switch for example and if we complete the job in say 6 hours I'll knock a little bit off the quoted cost, they like that.
 
I've just quoted a private landlord ÂŁ250, it's a 3 bed house. I always explain that I have to be thorough as it's important and need a day to do it right including the paperwork. Accepted immediately. :) But in that price we'd replace the odd damaged socket or light switch for example and if we complete the job in say 6 hours I'll knock a little bit off the quoted cost, they like that.

And the screw heads would be lined up :):)
 
According to a landlord customer of mine ÂŁ65. Can I beat that price she has been quoted ? :laughing:
I've just quoted a private landlord ÂŁ250, it's a 3 bed house. I always explain that I have to be thorough as it's important and need a day to do it right including the paperwork. Accepted immediately. :) But in that price we'd replace the odd damaged socket or light switch for example and if we complete the job in say 6 hours I'll knock a little bit off the quoted cost, they like that.

ÂŁ250.00 sounds about right Dave. Alas, it just isn't possible to get anywhere near that kind of price accepted around Glasgow, not when you have "landlord compliance certification" companies offering to do EICRs in three-bedroom properties for ÂŁ95.00.

I'm considering withdrawing EICRs from the list of services that I offer and withdrawing from this saturated market altogether as it's become a race to the bottom.
 

Reply to Yet Another Dodgy EICR in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
947
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I usually put something like this To assess compliance with BS7671 for continued safe operation (5 year periodical inspection)
Replies
8
Views
454

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top