Yes one more time! Cue rolling of eyes and yawning...
House is PME. 17th Ed dual RCD CU.
Two sheds: first one is 30m from house and requires only light and acouple of sockets.
Second and new shed is where it'll all happen and is a further 30m from the first shed. Customer will likely have ~4kw of PV on it, electric doors, heating boiler & small workshop etc here.
Plan:
o supply from the house CU via a non-rcd 32A MCB initially via 10mm SWA to the first shed CU. Main switch, 2 RCBO's, 1 MCB:
o from here via 32A mcb in 6mm swa to 2nd shed 5 way CU. Switch + RCBO's as required.
Q: does the palnel suggest exporting the earth from house entirely, or applying an earth rod at shed1 or shed2 and bonding armour to suit ?
I am favouring bonding the 10mm swa armour at house end, then applying an earth rod at shed1 to cover everything downstream of here but would like the panels opinion
House is PME. 17th Ed dual RCD CU.
Two sheds: first one is 30m from house and requires only light and acouple of sockets.
Second and new shed is where it'll all happen and is a further 30m from the first shed. Customer will likely have ~4kw of PV on it, electric doors, heating boiler & small workshop etc here.
Plan:
o supply from the house CU via a non-rcd 32A MCB initially via 10mm SWA to the first shed CU. Main switch, 2 RCBO's, 1 MCB:
o from here via 32A mcb in 6mm swa to 2nd shed 5 way CU. Switch + RCBO's as required.
Q: does the palnel suggest exporting the earth from house entirely, or applying an earth rod at shed1 or shed2 and bonding armour to suit ?
I am favouring bonding the 10mm swa armour at house end, then applying an earth rod at shed1 to cover everything downstream of here but would like the panels opinion