Ok guys been asked help mate out but i think he has done his install wrong but as misplace my regs book cant find exact regulations he contravines.
Scenario is this big boiler room and pre existing metal clad sockets in ring final circuit. 32 Amp protection.
He has added 6 FCU metal clad wired in 2.5mm swa. Across 50M of the room at various places as a radial circuit.
Instead of running cable back to the board intends to spur the 6 FCU from the nearest socket of the ring final.
Ive told him im pretty sure you can't spur more than one fcu from any socket.
Am i right ? If so anyone know specifically which reg this is against.
I need to get regs book out but being mainly machine based maintenance guy i dont do that many installs but seems wrong to me.
Thanks guys