Got called today to quote on a second fix of kitchen extention. On arrival all wiring was in place for lights extractor cooker. I have the start of the kitchen lights radial and the two legs of the ring to wire in as well.
I noticed that the cooker socket was not a dedicated radial but part of the ring. I asked client how the origonal electrician was going to link the ring in and was told he was going to extend the existing house ring to incorporate the kitchen so I asked to see the fuse board.
On looking it appears to be about 30 years old with the entire house sockets been supplied from one single 32A MCB which had replaced an old rewireable fuse in the board. (if you see what i mean)
So I said I dont believe the existing installation is capable of taking the extra load considering the age of it and especially because of the cooker being added to the ring. He then got a little defensive and started to say that he was only going to have a 3kw oven so was ok but i still said I was not happy.
What are your thoughts on this?
I want to split his tails feed another consumer unit, Put the new ring and lights on it as the existing installation is not rcd protected and there no space in the board and run in a new cable for cooker probably 6mm.
I know I should not mess with other peoples work etc so please constructive not destructive answers please
Thanks
I noticed that the cooker socket was not a dedicated radial but part of the ring. I asked client how the origonal electrician was going to link the ring in and was told he was going to extend the existing house ring to incorporate the kitchen so I asked to see the fuse board.
On looking it appears to be about 30 years old with the entire house sockets been supplied from one single 32A MCB which had replaced an old rewireable fuse in the board. (if you see what i mean)
So I said I dont believe the existing installation is capable of taking the extra load considering the age of it and especially because of the cooker being added to the ring. He then got a little defensive and started to say that he was only going to have a 3kw oven so was ok but i still said I was not happy.
What are your thoughts on this?
I want to split his tails feed another consumer unit, Put the new ring and lights on it as the existing installation is not rcd protected and there no space in the board and run in a new cable for cooker probably 6mm.
I know I should not mess with other peoples work etc so please constructive not destructive answers please