Hi everyone, firstly hope you all had a great New Year.
Wanted to get everyone’s thoughts on best design for Zappy EV charging point install.
Charging point is going to be installed at the bottom of a long driveway approximately 35 m from property meter and consumer unit.
The Earthing arrangement of the property is TT, .
Will be installing a 10mm SWA Cable from consumer unit location along brick wall down to the charging point location.
The charger point being Zappi has built-in type a 30ma RCD protection and 6ma d.c. protection .
Being TT, The armoured cable won’t comply to Ads If directly off a 40 amp MCB as Eli won’t be low enough so RCD required at 30ma for supply armoured 10mm cable .
Problem with this is now the discrimination (selectivity), this will now leave me with 2 30mA RCD’s in series, Which is definitely not best practice and doesn’t comply.
Ideal scenario would be to not have the 30 mA RCD at the charger point , But this is part of the printed circuit board in this particular charger.
Any advice on best practice to make sure all protection has been put in place but without having both our RCDs in series.
Thanks in advance
Wanted to get everyone’s thoughts on best design for Zappy EV charging point install.
Charging point is going to be installed at the bottom of a long driveway approximately 35 m from property meter and consumer unit.
The Earthing arrangement of the property is TT, .
Will be installing a 10mm SWA Cable from consumer unit location along brick wall down to the charging point location.
The charger point being Zappi has built-in type a 30ma RCD protection and 6ma d.c. protection .
Being TT, The armoured cable won’t comply to Ads If directly off a 40 amp MCB as Eli won’t be low enough so RCD required at 30ma for supply armoured 10mm cable .
Problem with this is now the discrimination (selectivity), this will now leave me with 2 30mA RCD’s in series, Which is definitely not best practice and doesn’t comply.
Ideal scenario would be to not have the 30 mA RCD at the charger point , But this is part of the printed circuit board in this particular charger.
Any advice on best practice to make sure all protection has been put in place but without having both our RCDs in series.
Thanks in advance