Zdb before dead tests. | Page 2 | on ElectriciansForums
Discuss Zdb before dead tests. in the UK Electrical Forum area at ElectriciansForums.net
swaley
Essex
Hi guys got my assesment in 3 weeks and want to get my testing spot on. Little confused whether to test Zdb on 2 way CU before dead tests?? Or do I jump straight into continuity? Thanks in advance.
I agree but not a abbreviation I ever quote. I believe it has been adopted where a true value of Ze cannot be established due to operational restrictions and the value is often referred to as Zdb which although often quoted is not a recognised abbreviation.
I have always taken Zdb as the measured EFLI at a DB to avoid confusion between Ze and Zs.
Ze would always Be Ze whether tested with the main earth disconnected or with parallel paths in place.
Although not a recognised abbreviation I've found it can save a lot of confusion. Especially handy when dealing with several DBs in an installation. If there was only one DB then there would only be Ze and Zs.
I think common sense is called for here. ............. its distinctly lacking in BS 7671
If you refer to a Zs - its the end of a circuit
If you refer to a Zbd - its obvious its at a sub board
So maybe it should be called a ZeZdb
Or Impedance at the DB Or more sensibly Zdb, what on earth is the argument for, after all it may not be a regulation but Z db makes sense to me
No Zs.
Reply to Zdb before dead tests. in the UK Electrical Forum area at ElectriciansForums.net
You need a galvanic isolator in the earth coming from the shore power. If using lithium batteries you will probably need a dc-dc charger to...
davesparks
That is true it is not really a practical class it is expected you have some knowledge of practical testing before the class. I do a lot of...