Hi guys, I'm at a job the now testing a d/b when testing a Zdb on a 3-phase board br- <0.01 bl- 0.09 gr- 0.09, what would cause such a difference in result, it comes from the meter to a busbar and then to the d/b, all 3 cables same size and same length of run, I will try to see if its slack connection when the power goes off but I doubt that will be the answer? Any thoughts guys cheers
 
You are near the resolution limit on your meter so a tiny change could cause this. Connection to the meter, make sure you are not on an oxidised section with your probes, or as you say it maybe just a slightly looser termination, but less likely.
 
Hi guys, I'm at a job the now testing a d/b when testing a Zdb on a 3-phase board br- <0.01 bl- 0.09 gr- 0.09, what would cause such a difference in result, it comes from the meter to a busbar and then to the d/b, all 3 cables same size and same length of run, I will try to see if its slack connection when the power goes off but I doubt that will be the answer? Any thoughts guys cheers



Not that i can see anything wrong with your tested values, but at those sort of values your probably not getting accurate values anyway, as your MFT or whatever, hasn't got the resolution to accurately measure values down to 0.01!!

Generally any differences in values will be normally down to the connections torque values, at these sort of low Zdb values.......

Check out this Sticky by IQ ....http://www.electriciansforums.net/i...38-higher-accuracy-low-ze-test-procedure.html
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Zdb dodgy reading
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
nicsin02,
Last reply from
Engineer54,
Replies
2
Views
1,438

Advert

Back
Top