I have a question about testing on a consumer unit from a distribution board, how would you do the Ze test at the second consumer unit ? I have heard a term Zdb but cant really find information on this.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Zdb Question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Ze would be taken as normal, it would be named Zdb though.
The old test result forms used to ask for Ze at origin, the new ones ask for Zs at DB.
Which to my mind is an improvement.
Still put Ze on the first page.
Zdb at the second consumer unit.
I assume you have the Ze reading for the main distribution board?
If you add Ze for the main distribution board to the R1 + R2 for the tails from Main Distribution board to the consumer unit that will give you Zdb.
Resistance aΩ + Resistance bΩ = Resistance cΩ.
No it won't, Zdb will also include the parallel paths to earth created by bonding extraneous parts.
I was asked this precise question by a C&G examiner this week. The examiner said my answer was correct.No it won't, Zdb will also include the parallel paths to earth created by bonding extraneous parts.
I was asked this precise question by a C&G examiner this week. The examiner said my answer was correct.
Measuring EFLI at the secondary consumer unit leaving all parallel paths connected would give a lower resistance than the sum of Ze from the main board and adding the R1+R2 for the tails to the secondary consumer unit. The purpose of Ze and therefore Zdb at the secondary board is to give the worst case scenario should, for some odd reason, all the parallel paths disappear. The Zdb can then be used for objective calculations for the operation of RCDs (for example).
Yes, a lower reading would make downstream circuits more likely to pass, but surely that is not the aim of the exercise?
I asked my assessor about 'calculated' and 'measured' Zs as my reasoning was as above. The calculated method [Ze+(R1+R2)] is likely to be a higher resistance value than the measured value due to the bonding still being connected with a 'measured' value. He stated that a 'measured' figure should be given although did not explain why.
We remove the bonding cables to get an accurate Ze and because we cannot presume the resistance value of the bonding will be a stable figure, however when we measure Zs we leave the bonding in place so we are using part of that 'instabilty' in our 'measured' value of Zs??
On ocassion the MFT will not record a Zs, then I can't see another option to using a calculated figure.