Hi all,
Please could someone explain this to me.
Scenario Primary Board--Db1-- Db2--Db3. (This is all hypothetical)
I have only just recently left the army, and have taken Electrical study's as my resettlement course and have achieved my 17th ED,2391, EAL Domestic, 2377, but realize i have a long way to go before i can call myself an Electrician. So please go easy on me.
I have taken a ZE reading at the Primary board, and taken Zdb at the remaining Dist boards, suppose i get a reading of 0.23 at Db2,i have been told that this is my Zs for Db3, and not Db2
So when im filling out Db3s schedule of test results,i should enter 0.23 for the Zs value in the box that's headed "to be completed if DB is not connected directly to the origin of the installation".
Thanks
Matt