Morning all,
Looking for some opinions
MK Sentry Dual RCD 63/30 CU
Fluke 1662 readings...
2 lead hi current Ze= 1.87 Ohms PEFC = 6A PSCC = 0.774kA
3 Lead no trip Ze = 12.95 Ohms
Zs at cooker/sockets = 12.56
RCD times are compliant
No electrode visible and Gas & H2O 10 mm at board.
Encountered this on Friday during EICR. Reading is high for TN-S but great for a TT. I was assuming it was a TN-S arrangement on visual inspection only to be confounded and concerned by the reading. What to record it as is my problem.? Is that armour of supply cable acting as an electrode or not? Also if I need to contact DNO.
Cheers all
Looking for some opinions
MK Sentry Dual RCD 63/30 CU
Fluke 1662 readings...
2 lead hi current Ze= 1.87 Ohms PEFC = 6A PSCC = 0.774kA
3 Lead no trip Ze = 12.95 Ohms
Zs at cooker/sockets = 12.56
RCD times are compliant
No electrode visible and Gas & H2O 10 mm at board.
Encountered this on Friday during EICR. Reading is high for TN-S but great for a TT. I was assuming it was a TN-S arrangement on visual inspection only to be confounded and concerned by the reading. What to record it as is my problem.? Is that armour of supply cable acting as an electrode or not? Also if I need to contact DNO.
Cheers all