Hi all, just after a little advice. Have been reading throygh some test papers in the office at work this week and came across a problem.One of our guys have tested a small train staion( i.e a cubical feeding a help point and 2x lamp post) its out in the middle of nowhere. Our guys who is off sick at the mo has put the system down as a TNC-S but it seems abit to far out in the sticks looking at the map, also the high Ze result he has recorded makes me think its in fact a TT system. The Ze was measured at 2.46 Ohms and Pfc at 0.10ka. Switching these results around using nominal voltage/Ze would roughly equal 2.3-4ka.Im thinking he has either the two results mixed up on a TT system or the Ze is really that high in which case what do you write on the test report as it would be the supply authority responsibility to reduce the measured value surely? please correct me if im wrong have been in electrics for 7 years only been testing for 5 months so still have alot to learn any help/advice would be great guys.