maharg
I carried out some work on some circuits for a new kitchen including extending a ring mains lighting circuit and a cooker circuit.These circuits were not connected at the time and had been installed over a period of time.
Kitchen had been gutted awaiting a new kitchen.
Customer wanted me to look at the remainder of the house circuits after kitchen install, so i decided to install henley block,new CU and leave the old CU in place awaiting to test and transfer old circuits.
Altough i am sure i tested Ze before starting when I went to connect extended circuits I got 33.1 ohms.
This is a TNS system,I checked all suppliers connections for tightness.
I know that Reg 411.5.3 states that max Zs for RCD is 1667 ohms for final circuits not exceeding 32A but how does this leave me with the 40A cooker circuit.
Also how does it affect my max Zs for the 60898 breakers.