M

maharg

I carried out some work on some circuits for a new kitchen including extending a ring mains lighting circuit and a cooker circuit.These circuits were not connected at the time and had been installed over a period of time.
Kitchen had been gutted awaiting a new kitchen.
Customer wanted me to look at the remainder of the house circuits after kitchen install, so i decided to install henley block,new CU and leave the old CU in place awaiting to test and transfer old circuits.
Altough i am sure i tested Ze before starting when I went to connect extended circuits I got 33.1 ohms.
This is a TNS system,I checked all suppliers connections for tightness.
I know that Reg 411.5.3 states that max Zs for RCD is 1667 ohms for final circuits not exceeding 32A but how does this leave me with the 40A cooker circuit.
Also how does it affect my max Zs for the 60898 breakers.
 
I carried out some work on some circuits for a new kitchen including extending a ring mains lighting circuit and a cooker circuit.These circuits were not connected at the time and had been installed over a period of time.
Kitchen had been gutted awaiting a new kitchen.
Customer wanted me to look at the remainder of the house circuits after kitchen install, so i decided to install henley block,new CU and leave the old CU in place awaiting to test and transfer old circuits.
Altough i am sure i tested Ze before starting when I went to connect extended circuits I got 33.1 ohms.
This is a TNS system,I checked all suppliers connections for tightness.
I know that Reg 411.5.3 states that max Zs for RCD is 1667 ohms for final circuits not exceeding 32A but how does this leave me with the 40A cooker circuit.
Also how does it affect my max Zs for the 60898 breakers.

I had a similar probem about 8 years ago, contacted the electricity supplier and they were able to change the service head and convert TN-S to TNC-S, my problem was earth sheath had corroded.

Another time someone had clamped the armouring, when the actual earth was a copper sheath within the armoured.

Anyway first step contact Suppliers, in the meantime connect all circuit very RCD, until you can sort out problem.
 
I had a similar probem about 8 years ago, contacted the electricity supplier and they were able to change the service head and convert TN-S to TNC-S, my problem was earth sheath had corroded.

Another time someone had clamped the armouring, when the actual earth was a copper sheath within the armoured.

Anyway first step contact Suppliers, in the meantime connect all circuit very RCD, until you can sort out problem.
Thanks for advise I have connected all circuits and they are RCD protected but to safeguard myself I would like to fill out EIC .
If I fill out EIC with high zs readings and comment that the Ze is high and DNO have been contacted am I covered
 
Thanks for advise I have connected all circuits and they are RCD protected but to safeguard myself I would like to fill out EIC .
If I fill out EIC with high zs readings and comment that the Ze is high and DNO have been contacted am I covered

Please before completing EIC contact the technical dept / engineer at DNO for advice.

33.1 ohms is not acceptable and it well probably get worse, I would not be happy to leave the Ze as it is, if the DNO are unable to do anything or unwilling, you may have to convert installation to a TT (install your own earth electrode, either rod or plate)

Please do not leave it as it is, if the customer lost there earth and a fault occurred, it could be fatal. it could cost you 300K and 5 years for manslaughter
 
Please before completing EIC contact the technical dept / engineer at DNO for advice.

I have contacted DNO who will be arranging a call to premises.
I would still like to know how I safeguard my self.
This problem could be just with this adress or the whole street.
Someone with no RCD protection next door could be at risk,so by contacting EDF I acted with due diligence but should I record my readings or just wait until it gets better.
I might not be able to return to the premises for 2 or 3 days after EDF have been.
 
I have contacted DNO who will be arranging a call to premises.
I would still like to know how I safeguard my self.
This problem could be just with this adress or the whole street.
Someone with no RCD protection next door could be at risk,so by contacting EDF I acted with due diligence but should I record my readings or just wait until it gets better.
I might not be able to return to the premises for 2 or 3 days after EDF have been.

You say all circuits are RCD protected and tested if you complete EIC then when EDF call and decide to change to TNCS or tell you to convert installation to a TT, your certificate will be worthless.

So if your completing generic certificate and not NIC, ECA etc numbered form then complete cert by all means, but it may be worth you writng to the customer explaining why you have not issued EIC.

Yes rest of the street could be effected, if you worried maybe pop next door and ask if you could check their supply, it may get you more work.

As long as all circuit are RCD protected your covered and you have informed client in writing about problem you be fine.
 

Reply to Ze 33.1 Ohms in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
743

Similar threads

If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K
  • Question
With what looks like only 5 circuits you can probably put a little 5 way garage consumer unit in there if money is tight
2
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top