Ok I've got 2 supplies with continuity between the various earthing arrangements on both sides but I can only find 1 MET. one side is 3 phase and the other is single phase. the MET is on the single phase side which has a TN-s earthing system. the other side has a TN-C-S earthing system. on the single phase TN-S side with the MET I am getting a reading of .54 for Ze which is acceptable for TN-S but not TNC-S. There is a piece of fixed furniture in front of the TNC-S CU which is preventing me from taking a direct measuement of Ze on that side but the client is desperate to keep his seating arrangement as is. I could take an r1 + r2 and subtract from Zs (Zs-(r1+r2)=Ze).

Any ideas???
 
On the supply that you state is TNC-S you say that the Ze is 0.54.
Take an external impedance reading between L - N on this supply and compare this to the Ze reading both should be approximately equal if it is a TNC-S.
The reason i am saying this is that a reading of 0.54 L - N seems very high for any type of system.
Point is are you sure it is TNC-S.
 
Last edited:
Let me start by apologising for the way I have explained this.:eek:

OK sintra its the TN-S side that I have managed to measure the Ze on which is why .54 is considered acceptable ( less than 0.8). The reason I say its TNC-S on the other(3Phase) side is that it says either PME or PEN either way that makes it TNC-S no?
 
Just a thought perhaps the continuity between the earthing systems is being achieved through external paths which would mean that there could be no earthing on the 3 phase side???
 

Reply to Ze again in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
789
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
810

Similar threads

N
  • Question
In my first sparking era (late 90's) I was always told to run a neutral to the isolator, as the chances are whoever is using the machine will...
    • Like
2
Replies
21
Views
1K
The actual listed observations seem easily resolvable, comfortably less than a day's work. The picture of the supply poses a few questions...
Replies
5
Views
998

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top