Please can someone clarify this please.

I test all three phases on (LE) setting giving me 3 ze readings and 3 pefc readings. I then test all three phases on (LN) setting giving me 3 ze readings and 3 pscc readings.

Record the highest reading of the 6 ze readings.

Then take the highest reading of all 6 pfc readings and double it. Or do you only double the pscc reading?? I've searched the answer and not found a clear verdict.



Also when doing zs readings on outgoing circuits is it better to have my fluke 1651 set to LN or LE. I do the later, however this is somewhat more time consuming??

Any clarification wold be appreciated
 
Please can someone clarify this please.

I test all three phases on (LE) setting giving me 3 ze readings (this is all you need for Ze the highest of the 3 is recorded) and 3 pefc readings. I then test all three phases on (LN) setting giving me 3 ze readings (not required)and 3 pscc readings.

Record the highest reading of the 6 ze readings.(You will only have 3 as you don't do L-N)

Then take the highest reading of all 6 pfc readings and double it.(correct) Or do you only double the pscc reading?? I've searched the answer and not found a clear verdict.



Also when doing zs readings on outgoing circuits is it better to have my fluke 1651 set to LN or LE. I do the later, however this is somewhat more time consuming??

Any clarification wold be appreciated

In bold above
 
Ze, Zdb and Zs are all earth loop readings used to establish that the resistance is sufficiently small to operate the breaker / fuse in the correct time. Some testers can do line to line testing to get PSCC, otherwise LNx2 as LN is usually higher than LE.
Not sure why you are testing loop through neutral, i only do this if i cannot get a reading on LE to make sure tester has not lost the plot.
 
On a three-phase installation the PSCC will always be greater than the PEFC. If the PSCC cannot be measured directly between phases then double the highest line-neutral short circuit current.
 
Ze disconnect the earthing conductor then test if you have permission to isolate with earth fault loop setting of your tester set on High loop if no RCD upstream
L1-E
L2-E
L3-E
then reconnect the earthing conductor
then set your test instrument to PFC test high
no need to test PEFC between
L1-E
L2-E
L3-E
you dont need to do this as the the PSCC will always be higher on a 3 phase board
so jsut test PSCC
Eg
L1-N = 3.0kA
L2-N = 3.1kA multiply by 2 and thi is your pfc as this is the highest =6.2kA
L3-N = 3.0kA

reason we multiply by 2 is the PFC will always be igher between the lines and as your not supposed to measure between the lines as not all testers can do this we multiply by 2 which errs on the side of safety
really its more ike 1.732 which is the Sq root of 3 so by multiply by 2 if your protective devices can carry 6.2kA then they comply Icn and Ics
 

Reply to Ze and pfc test on 3 phase board. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
514
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

Having some issues with my companys fluke 1662/1663 tester. Zeroing 2 leads for continuity test we get the value 0.08 which is expected. The issue...
Replies
0
Views
295
FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top