Today I have tested a new installation in a block of flats (ground floor). When I took a Ze reading the meter read 0.00.
I have taken this to be 0.01 as this is the lowest credible reading possible on my meter. When I tested PSC the meter read OL or out of range.
My question is can I use Ohms law to calculate the PSC and do I log the result as >'the result' or just 'the result'..
I know it sounds a bit fussy but we have an NICEIC inspection soon so need to be on the ball.
Thanks for your help.
 
So what breakers you gonna use on that then?

Big & expensive un`s methinks :D

Seriously, Dogleg, i wouldn`t `assume` its 0.01 - or anything else. Your name will be on that EIC saying you`ve checked compatability of Pfc arresting device against established max Pfc.

What are the breakers Icn rated? Whats the supply cable. Those values suggest you`ve got a good, clean earth if nothing else :)

I`d suggest you first check your meter on another install, or try another meter in the one you mentioned. If AOK you`re gonna have to establish what the max PSCC actually is someway or other. You could always try the DNO :confused:
 
Dont know what meter you have, but with my Fluke 1651 you can toggle between 10KA & 50KA limit for EFLI by pressing the on/off button and F2 at the same time.

Default is 10KA so have never changed the setting, but wonder if it will allow readings to be taken instead of 'out of range'?

EDIT-

Was also wondering if by selecting 50KA on a Fluke, will it provide a more accurate result when testing supplies of >10KA?
 
Last edited by a moderator:
Today I have tested a new installation in a block of flats (ground floor). When I took a Ze reading the meter read 0.00.
I have taken this to be 0.01 as this is the lowest credible reading possible on my meter. When I tested PSC the meter read OL or out of range.
My question is can I use Ohms law to calculate the PSC and do I log the result as >'the result' or just 'the result'..
I know it sounds a bit fussy but we have an NICEIC inspection soon so need to be on the ball.
Thanks for your help.

As mentioned check your tester!!!! bats are gone a think!!!

your pfc is 230/ ze so 230/.01=23000 :eek: had high readings in top floor flats but never the bottom!!
 
yes got another loop tester on the board today and exactly the same..0.01 at the top of main switch also took reading at cut out with 16mm earth disconnected and the same..0.01!!
can get a very high Earth Fault reading (18KA) but no short circuit reading..out of range (>20KA)..
I think we will have to contact the supply company to sort this out..
Surely they shouldnt supply with this low Ze??
Do you know what are the highest rated 60898s or equivalent?
Thanks for your time
 
yes got another loop tester on the board today and exactly the same..0.01 at the top of main switch also took reading at cut out with 16mm earth disconnected and the same..0.01!!
can get a very high Earth Fault reading (18KA) but no short circuit reading..out of range (>20KA)..
I think we will have to contact the supply company to sort this out..
Surely they shouldnt supply with this low Ze??
Do you know what are the highest rated 60898s or equivalent?
Thanks for your time
pfc live to neutral and if 3 lead tester earth onto neutral???

ze disconect main earth from main earth bar???

is another flat into your earth block seen this many times where the main earth jumps into another
flat!!!!

stupid ? is the supply earth tight???
 
yes all testing done correctly..3 lead tester black AND green to Neutral bar and red to top of main switch live..
Supply earth is tight..if it wasnt wouldnt Ze reading be higher and therefore Pfc be lower??
 

Reply to Ze and PSC in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
752

Similar threads

The actual listed observations seem easily resolvable, comfortably less than a day's work. The picture of the supply poses a few questions...
Replies
5
Views
996
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top