Today I have tested a new installation in a block of flats (ground floor). When I took a Ze reading the meter read 0.00.
I have taken this to be 0.01 as this is the lowest credible reading possible on my meter. When I tested PSC the meter read OL or out of range.
My question is can I use Ohms law to calculate the PSC and do I log the result as >'the result' or just 'the result'..
I know it sounds a bit fussy but we have an NICEIC inspection soon so need to be on the ball.
Thanks for your help.
I have taken this to be 0.01 as this is the lowest credible reading possible on my meter. When I tested PSC the meter read OL or out of range.
My question is can I use Ohms law to calculate the PSC and do I log the result as >'the result' or just 'the result'..
I know it sounds a bit fussy but we have an NICEIC inspection soon so need to be on the ball.
Thanks for your help.