Evening, if say for example I had a ze figure of 1.0 at origin, and I had a Zdb from a sub main to dist board figure of 1.1. To calculate zs is the calculation zs= ze+Zdb+ r1+r2 for the individual circuits.

Many thanks
 
Yes mate
for a DB supplying a sub board its
Zs=Ze + (R1 + R2sub main) + (R1+ R2final circuit)
the SUB MAIN R1 + R2 IS THE ZDB ALSO fir that board
So measure your Zdb and add to the R1+R2 of final circuit and thats your ZS for the final circuit
 
Sounds good to me: Zs is the whole impedance, Zdb is the impedance up to the DB where a distribution circuit is involved, Ze is the impedance external to the installation and hence measured at the point closest to the service head. Only thing to watch out for is that you don't count the impedances twice; ie Ze+Zdb. Zdb to my knowledge is the external impedance + the resistance of the distribution circuit conductors (R1+R2). So unless you're going to measure R1+R2 on the distribution circuit (which'd require safely isolating the distribution circuit cable) then add to Ze to get Zdb I'd measure Zdb live then add R1+R2 on the final circuit to get your Zs.Hope this helps.
 
Hi Guys
Sorry this may be a silly question, but I recently installed a main C/U on a TT system and a sub C/U board in an out building. Both of these systems or on seperate rods and are only connected to there indiviual earth rod, so when i'm trying to calculate the Zs on a final circuit is the sum: R1 + R2 of the supply cable to sub board + Ra of sub board + R1 + R2 of sub board final circiut??
Sorry for this long winded post, your help with would be appreciated

Many Thanks
T&E
 

Reply to Ze and zdb in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
732
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
972

Similar threads

For a new circuit or alteration the dead tests should be done first to ensure it is safe to energise.
Replies
3
Views
327
For what OCD? There may be other means of over current protection that allow a Zs of0.45 (HRC Fuse?)
Replies
3
Views
506

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top