Ze in BRB | on ElectriciansForums
  • Thread starter brucegenerator
  • Start date
  • Replies 15
  • Views 2K

Discuss Ze in BRB in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

B

brucegenerator

Could any one tell me which page or chapter to find maximum Ze of circuit breakers please in BRB?
 
If you mean max Zs, starts around page 48 from memory, but make sure you use the correct table for device/earthing system.
 
Zs is the one is it table 41 page ?cheers!

There is no table 41 by itself, only 41.1 , 41.2, 41.3, etc etc. Regarding Ze there are only 3 max values of any relevance

tn-c-s - 0.35 ohms

tn-s - 0.8 ohms

and TT - more confusingly a max of 21 ohm for the distributor's earth electrode , with the consumer's earth electrode being as low as possible. A figure of 200+ ohms is considered to be unstable and 100 ohms is often considered to be the max acceptable. Page 11 of the OSG shows this.
Table 41.5 of the BRB shows Zs for values for rcd operation in final circuits not exceeding 32A
 
Never felt the need to fork out 50 bucks for something i would hardly use .Just needed the page number for my 2391 practical.That is all.Got the GN3 ANYWAY.
 
find myself costantly refering to bs7671 and osg, even on standard installations i cover every day, for zs values that are mentioned for a start.

And as lenny state all competent per schemes require you to hold a copy.
 
Last edited by a moderator:
I can't see how anyone can carry out installation work to comply with bs 7671 if they don't have a copy.

Except rain man possibly.
 
The regs nowadays apear to contain information on what complies,but little in the way of how to comply

In the past it was "thou shalt do this" and "thou shalt do that"and working out for yourself was minimal

To apply the regs to installations present day,a person needs to continually refer to those regs to see if what he proposes conforms to whats required
I realise how tight money can be, but not owning or wanting a brb,even if you have many years in the trade, it is surprising, and as posted,it is a requirement if you were to join any of the schemes,so may be worth an investment by yourself
 
I cant remember them ever saying what to do, only what not to do and thats the 15th/16th and 17th. Thats why we have the OSG. But I agree with your point that it is always worth having it to refer to, as you cant beat the 'real' regulation wording rather than the OSG version. You cant always get the right flavour of the Regs with the Guide in some instances.:eek:
 

Reply to Ze in BRB in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
810
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

On the minor works in the brown book it has Zdb
Replies
3
Views
296
I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
254

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top