B

bobby101

hi all as the title suggest i was at a second floor flat, doing a pir when i did the ze test the machine i was using the metrel mi3125 gave a buzzing noise to suggest that there was voltage present on the main incomer earth, but the meter did not show a voltage is this a meter at fault or is it somthing that iam missing .. ohh yeah after this was done i reconnected the main earth and tried todo a zs test on a ring circuit and i got a result no probs ( btw, i had done three pirs before this one in the same building and got no probs) also what do i mark down on my pir for this do i have to calculate ka and just note this down in the cert i am at a unsure what to do so any help will be greatly appreciated
 
Not quite sure what you're saying but I can see it possible to get a Zs reading when theres no Ze. parallel paths

Best example is a house near Redditch, TT, Ze 17.8 Ohms.

Do a Zs at a socket under the DB, 0.47 Ohms.

Turns out the water mains is connected to a house over the field (the water board tried to meter them but decided it would cost to much to split it), and guess what earthing that house has, thats right, TNCS. And theres a main bond to the water service :disguise:
 
If a Metrel is showing a voltage to earth then this is often down to a static charge on the user, if you press the test button through an insulator then the test should work. Try covering half the button with sellotape and only press that bit if there is a problem (the rest of the time it takes the earth from the user). or just press the button with your insulated screwdriver.
 

Reply to ze- no, zs- yes ?? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
818
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
884

Similar threads

Hi Dave thanks for the info I revisited the premises to change a cooker switch and redone the test from the MET with MET disconnected from DB...
Replies
16
Views
1K
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top