Hi Guys

I know that if you have a main DB feeding a 2nd DB, then the Ze for the 2nd DB is:
Zdb = Ze from origin + (r1 +r2) of the cable supplying the 2nd DB. Or measured Zs at the second boards supply. But how do you then get Ze for, say a 3rd DB fed from the 2nd and then Ze for a 4th DB fed from the 3rd etc? :confused:

Any advice would be appriciated:)
 
2nd DB - Zdb = Ze (Origin) + (R1 + R2) of cable supplying 2nd DB

3rd DB - Zdb = Ze (Origin) + (R1 + R2) of cable supplying 2nd DB + (R1 + R2) of cable supplying 3rd DB

4th DB - Zdb = Ze (Origin) + (R1 + R2) of cable supplying 2nd DB + (R1 + R2) of cable supplying 3rd DB + (R1 + R2) of cable supplying 4th DB

.....and so on ;)
 
Last edited by a moderator:
Cheers Guys,

So basically after the first board your Ze at the others is actually the Zs reading of the cable supplying that particular board. Nice one.
 
Yep on a periodic report,you will find ZS reading and pfc for that db,so zs at that point would be the sum of ze at origin plus R1 & R2 of the sub main circuit to next db and so on,but ze is only taken at origin.
 

Reply to Ze of 3rd , 4th db etc in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
789
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
810

Similar threads

  • Question
Thank you for the advice; I did figure it would be in the realms of discovering, say, a 10mm earth cable in a property, and having no more...
Replies
2
Views
853
  • Question
Just re-read the OP's post and it is an existing 5C SWA so presumably a 3P supply. For 40A and 150m you are seeing 6.6V drop or 1.65% of 400V 3P...
Replies
8
Views
877

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top