J

jenions

first time ive came across this so just wondering what i should do? measured a ze of 0.8 on a tn-s so its border line max value is it safe to leave or will it cause issues if left? apologies if its a stupid question, its the silly things that catch you out
 
a call to DNO expressing concern that it could go above 0.8 might be a good idea. (CYA)
 
Report it to the DNO, you will have discharged your duty of care on behalf of your customer and that way it won't rebound at a later date. Remember to record your actions as an appendix to your certificate/report.
 
the DNO have a duty to maintain any earthing arrangement they supply, so they should not charge. as long as you have informed them (in writing is best) then you've covered your arse. as markie says. note it on the report.
 
As its within dno guidlines i doubt they would be too concerned so i wouldnt worry youve recorded on your cert but if the higher ze is causing too high zs values then chase it up
 
Just a thought but what Instrument are you using? Is it a Fluke

I had my assessment last week and my assessor mentioned something that I didn't realise I had to do. If you have a Fluke then the ELI test facility on the meter needs nulling, if not done it can give false high readings.
 
Last edited by a moderator:
Also have you measured it on the main earth alone ? and not with all the earths commoned I measured 0.9 on a job and told the owner after the DNO sorted it out to inform the guy downstairs because he could have been in the same situation as him but now he has his earth sorted out and his water and gas pipes (that run through the guy downstairs) earthed he now has a good earth through his bonding to the gas and water
 
Just a thought but what Instrument are you using? Is it a Fluke

I had my assessment last week and my assessor mentioned something that I didn't realise I had to do. If you have a Fluke then the ELI test facility on the meter needs nulling, if not done it can give false high readings.

It mentions this in quick start guide, the zero adaptor guide and the full instruction manual. If you've zero'd it against a wander lead at some point, it might also be giving false lows which could mean a re-check of some results might be required.
 
got megger 1552 so no worries about the fluke and i got 0.8 with just main earth, nothing connected. if DNO will do it foc then thats ok, its going to be my assesment job and they come on 12th oct so gonna ring nic assessor check his opinion
 

Reply to Ze on Tn-s in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
839

Similar threads

Thanks I re tested this morning as I had other bits to finish off . I tested three times and it was 0.30 every time . It may have been my leads...
Replies
7
Views
2K
  • Question
I think I might be tempted to test this theory, if it can be done without causing danger to anyone.
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top