Hi all,
I recently went to install a new circuit & when trying to obtain a ze reading at the origin (TN-C-S) I got 0.01 ohms with a pfc of >19.9kA... This is when testing from the main distribution board which is in a hut next to the building where the work took place 15/20 meters away. Anyone came across this type of scenario before!?
Cheers
 
Modern testers are not good at measuring low impedance values of Ze caused by being close to the substation of which a factory may have its own. As Wilko said introduce a known resistance to the test and deduct this from your reading but if you are close to the source substation it will be low.
 
Cheers Wilko, Westward... when I test from DB1 in the factory itself, the readings go back to normal which tells me its not my tester. It is close to the substation actually, didnt realise this would give me a high pfc & low ze! So a possible option to find a more accurate reading would be to calculate the difference between the R1+R2 & Zs @ the first DB in the factory? If so, how would I go about calculating a lower pfc taking into consideration its a three phase supply?
 
Yes I have come up with low Ze in a domestic. Sub station 100 yards away. If you look at your manual you may see it specifies that the reading you are taking is within six figures. Meaning your reading may be .07. I or the customer had a new cut out by the DNO and when they read it it was .11 (Ze) I spoke with the tech at Kewtech and they pointed the figures thing. So my reading was .03 and of course there were concerns regards the Ics/Icw of the MCBs. But if I/you think about it if I add the six figures I am not that far away from the DNO figure. It would seem we are at such a fine level of measurement it is very hard to really get an accurate figure in those circumstances.
 
Cheers Wilko, Westward... when I test from DB1 in the factory itself, the readings go back to normal which tells me its not my tester. It is close to the substation actually, didnt realise this would give me a high pfc & low ze! So a possible option to find a more accurate reading would be to calculate the difference between the R1+R2 & Zs @ the first DB in the factory? If so, how would I go about calculating a lower pfc taking into consideration its a three phase supply?
You could use the R1+R2 of the board submain but I would personally use a known resistance of say 0.10 and introduce this to the test then deduct it. It is bound to be low if you are in close proximity to the transformer.
 
Calculate it from your Ze. My old Robin tester rarely gets thrown by low impedance Ze, don't make em like they used to.
 
I wouldn't worry about the ka ratings of the mcbs too much as back up protection can be with manufacturers guidance be achieved by the fuse in the cut out which will clear the fault
The conditional rating is 16kA so beyond that you cannot assume that they will withstand the fault current. I would ascertain the figures by enquiry - measurement simply won't be accurate.
 
The conditional rating is 16kA so beyond that you cannot assume that they will withstand the fault current. I would ascertain the figures by enquiry - measurement simply won't be accurate.
A type 2 bs 1361 for example has a typical ka rating of 33ka so I think it will.
Like I've said manufacturers should be consulted if back up protection is used
 

Reply to Ze / PFC conundrum at factory in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
778
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
789

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top