P

Piratepete

Hi Guys

The PME 100Amp 3 phase supply at the meter in my local church has a Ze of 0.3, 0.29 and 0.33 Ohms at the meter for each of the 3 phases.

I'm proposing a 3ph DB 20 metres away (in a new annnexe) via a 40 Amp switchfuse by the meter.

As Ze has to be measured at the DB I have a problem because the 4 core SWA 6sqmm supply cable I was going to use will add 0.27 Ohms - the total then easily exceeding the max allowance 0.35 Ohms. Even if I use a 10sqmm cable I will be adding 0.16 Ohms.

Am I correct in my musings. Any solution? The church supply cannot be improved! Would it be allowed to give the new DB a TT earth even though the annex is only separated from the main building by a door?

Thanks
Pete
 
Ze is taken at the origin of the installation (which you have already tested)!! Any board/CU downstream is classed as Zs or commonly referred to as Zdb!! So as long as your Zs values meet the minimum allowable for your protective devices your fine to go!! lol!! Don't they teach this at collage anymore??

Don't forget, with a PME supply, if this extension to an annex, is outside of the current equipotential zone and has extraneous services such as water/gas pipes or the like you will need at least a 10mm bonding conductor to run with your 6mm SWA cable, or increase the SWA cable size and core number to suite!! lol!!
 
Last edited by a moderator:
You're creating a problem where there isn't one!

Z[SUB]e[/SUB] only exists at the intake.
The EFLI at your new board is a Z[SUB]DB




[/SUB]
edit...got to be quick around here! Eng already answered! :)
 
Thanks
Not thinking straight!. Years of measuring Ze at the mainswitch and calling that the 'origin' has addled my brain!

Yes - I do need a seperate 10mm bonding conductor, pain in the a that it is.

Note that the new Generic Schedule of Test Results now asks for 'Zs at the DB' and not 'Ze at the Origin' like it used to do.
 
Last edited by a moderator:
Just to be clear and I know you are probably aware of this Piratepete, Z[SUB]e[/SUB] is measured with the main earthing conductor disconnected from the main earthing terminal.

P.S Archy, check me out with my subscripts, two can play your game ;)

John
 
Thanks
Not thinking straight!. Years of measuring Ze at the mainswitch and calling that the 'origin' has addled my brain!

Yes - I do need a seperate 10mm bonding conductor, pain in the a that it is.

Note that the new Generic Schedule of Test Results now asks for 'Zs at the DB' and not 'Ze at the Origin' like it used to do.

Ze and Zs are two completely different animals!! lol!!

Zs at a DB/CU is commonly called Zdb, but is still in reality, a normal Zs test with all bonding and other parallel earths in place. The Zdb notification, is just indicating that the value indicated was taken at the DB/CU...
 
Just to be clear and I know you are probably aware of this Piratepete, Z[SUB]e[/SUB] is measured with the main earthing conductor disconnected from the main earthing terminal.

P.S Archy, check me out with my subscripts, two can play your game ;)

John

¡sʇdıɹɔsqns ʎɔuɐɟ ɹnoʎ ɥʇıʍ noʎ ʇǝפ
 

Reply to Ze Problem for Extended Supply in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
108
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
905
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top