P
Piratepete
Hi Guys
The PME 100Amp 3 phase supply at the meter in my local church has a Ze of 0.3, 0.29 and 0.33 Ohms at the meter for each of the 3 phases.
I'm proposing a 3ph DB 20 metres away (in a new annnexe) via a 40 Amp switchfuse by the meter.
As Ze has to be measured at the DB I have a problem because the 4 core SWA 6sqmm supply cable I was going to use will add 0.27 Ohms - the total then easily exceeding the max allowance 0.35 Ohms. Even if I use a 10sqmm cable I will be adding 0.16 Ohms.
Am I correct in my musings. Any solution? The church supply cannot be improved! Would it be allowed to give the new DB a TT earth even though the annex is only separated from the main building by a door?
Thanks
Pete
The PME 100Amp 3 phase supply at the meter in my local church has a Ze of 0.3, 0.29 and 0.33 Ohms at the meter for each of the 3 phases.
I'm proposing a 3ph DB 20 metres away (in a new annnexe) via a 40 Amp switchfuse by the meter.
As Ze has to be measured at the DB I have a problem because the 4 core SWA 6sqmm supply cable I was going to use will add 0.27 Ohms - the total then easily exceeding the max allowance 0.35 Ohms. Even if I use a 10sqmm cable I will be adding 0.16 Ohms.
Am I correct in my musings. Any solution? The church supply cannot be improved! Would it be allowed to give the new DB a TT earth even though the annex is only separated from the main building by a door?
Thanks
Pete