planetman
Hi Could anyone answer this query? We are looking to replace a cable that has gone down. The cable is fed from a section board (protected by a a square "D" CNAE34125 125amp) which in turn is fed directly off the HV transformer (11kv-433V) in the adjacent room (max 3m metres length of cable).
The supply cables to the section board are 500mm singles with approx 2X150mm earth.
The Ze is reading 0.17 at the incoming main switch. The problem is the manufacturers Zs reading for the 125amp MCCB is 0.18. The Zs reading at the D.B which is fed from this breaker is 0.44.
What Ze reading should we expect at the incoming supply? Under normal circumstances 0.17 would be great.
Any help on this would be appreciated, Cheers
The supply cables to the section board are 500mm singles with approx 2X150mm earth.
The Ze is reading 0.17 at the incoming main switch. The problem is the manufacturers Zs reading for the 125amp MCCB is 0.18. The Zs reading at the D.B which is fed from this breaker is 0.44.
What Ze reading should we expect at the incoming supply? Under normal circumstances 0.17 would be great.
Any help on this would be appreciated, Cheers