MEGGER?

Using a Megger 1502, How would I carry out this test on a TT system. I am unsure of lead positions on tester. I am fairly new to electricals being a plumber, but would appreciate anyones help/advice.
 
Live Test and No Earthing so Extra Care

1 Isolate Supply
2 Disconnect the earthing conductor
3 Set the instrument to loop test
4 If you are using a two-lead instrument the leads should be
connected Black lead to disconnected earth and red to live incomer.
If you are using a three lead which I think the Megger is​
then join black and green test leads together.
5 The measurement obtained is Ze and can be entered on the test
certificates in the appropriate place.
6 Reconnect the Earthing Conductor
 
A Ze test can only be carried out on an existing earth electrode (i.e, periodic inspections), if you have installed it then you must purchase an earth electrode tester and carry out the procedure according to G3 - 2.7.12.

When testing an earth electrode precautions must be in place as you will be introducing gradient voltages to earth. I would leave this to a qualified electrician with experience in said.
 

Reply to Ze Question. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
250
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
723
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
695

Similar threads

Having some issues with my companys fluke 1662/1663 tester. Zeroing 2 leads for continuity test we get the value 0.08 which is expected. The issue...
Replies
0
Views
252
  • Question
Please do remember to account for diversity in all this - with 1200 and 2000A incoming services I’d be surprised if you do actually need to uprate...
Replies
10
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top