Thanks Malcolm, seems your in the same neck of the woods as me. Im in Ashford, Kent.

Yes the whole installation is covered by a 100mA RCD. I have made a note of the cert as the RCD is not type S. One other issue ive had to record on my results is the playhouse which is supplied from my unit does not have an RCD at its CU. This means the playhouse is only covered by the 100mA at the house. Ive made a note of it, but am I responsible for this, i.e shouldnt connect the p/house until a 30 mA is fitted? The playhouse CU supplies has one 32A Ring and one 6A Lighting circuit. The sockets are the issue as theyre likely to supply outdoor equipment.

Many thanks,

Rob

Rob look at page 4 of the Regs in the introduction, concerning the existing installation, it tells you that because it does not conform to the new BS 7671-2008, but perhaps to an earlier edition, in this case possibly the 16th, then it does not make it unsafe to use or require upgrading

That playhouse is protected by the upfront 100mA RCD, providing you have tested it and it conforms to the correct operation times then there is no need to worry about connecting it back up.

Yes agree that you should inform the customer that there is not the 30mA additional protection recommended by the BS 7671-2008, and for perhaps a safer installation for a few pounds you can upgrade it to the new regulations, but you have tested the 100mA RCD, and if it was good then there is no need to change the status quo.Then just note it on your EIC in the section for existing installation.
 

Reply to ZE+(R1+R2) Sub-mains? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K
  • Question
Many thanks all. Very helpful to be able to bounce these things around. Was fairly happy with it all initially, but once the seed of doubt is...
Replies
8
Views
827

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top