Hi, I've done some work for a customer and am testing the circuit for the MWEIC. When doing the Ze the 30mA supply RCD is tripping leaving me with no result.
A little about the installation: The property is in a group of 12 or so properties that are holiday lets. All of the properties are fed from a switch room in the site Laundry building with a 30mA RCD protecting each installation located in a meter box on the side of each building along with a meter. All of the properties have TT earthing arrangments. Now I can get a Ze (105 Ohms) result if I test on the meter side of the RCD (RCD 'off' and earth disconnected from Henley block) but when I try testing from the CU (installation isolated and Earth disconnected) I just trip the RCD.
My question has 2 parts,
1: does anyone know a way around this?
2: Is it acceptable to do an R1+R2 on the feed + earth from the RCD to the CU and add that to the Ze I have. Record that result as the Ze and make a note on the MWEIC. I would then have to do the actual R1+R2's and add it to the overall Ze as I expect I will get a trip doing Zs tests as well.
I haven't gotten as far as doing any tests on the RCD I will do them when I return to the property this week.
Thanks in advanced
A little about the installation: The property is in a group of 12 or so properties that are holiday lets. All of the properties are fed from a switch room in the site Laundry building with a 30mA RCD protecting each installation located in a meter box on the side of each building along with a meter. All of the properties have TT earthing arrangments. Now I can get a Ze (105 Ohms) result if I test on the meter side of the RCD (RCD 'off' and earth disconnected from Henley block) but when I try testing from the CU (installation isolated and Earth disconnected) I just trip the RCD.
My question has 2 parts,
1: does anyone know a way around this?
2: Is it acceptable to do an R1+R2 on the feed + earth from the RCD to the CU and add that to the Ze I have. Record that result as the Ze and make a note on the MWEIC. I would then have to do the actual R1+R2's and add it to the overall Ze as I expect I will get a trip doing Zs tests as well.
I haven't gotten as far as doing any tests on the RCD I will do them when I return to the property this week.
Thanks in advanced