Testing for cu change .Customer had eic for 2 wy rcd protected cu fitted for kitchen sockets when refurbed a year ago. no prob but noticed the ze had been put down as 0.41(tncs) bit high so i tested on high current as always 0.21 changed to no trip 0.42. ive never test ze on no trip as high current gives a more accurate value.
i just wondered what setting others use when testing ze.
cheers
neil
 
Not sure why you'd want to test Ze on no-trip loop setting. Doesn't make a lot of sense.

But I agree with you that non-trip loop can give sky-high readings at times.
 
Exactly i can only think that the person who took the reading for kitchen refurb must have had his tester on no trip as when i took measurement on no trip it was 0.42 approx the same. Wouldnt you query this if you got. Such a reading on a tncs. As well as that the value of main fuse was incorrect and all the schedule of inspection items were tick including selv/pelv not a 12v in the house and some items u wouldnt except to be applicale in domestic. This was filled in by a niceic fully approved company looks like the certs were filled in before job was done
 
Last edited by a moderator:
Ze can never need the no trip setting, though I did not realise it could make such a difference, I thought it was just a little bit high.
I would only do it If I was rechecking later and forgot to change the setting!
 
exactly the reason i asked queston was result on eic for kitchen obviously person who tested it stll had tester on no trp when checking ze but wouldnt you realse something bt odd with ze being 0.41 on a tncs and also the pfc on eic was 1.1ka a result you would get from a much lower reading of ze. just thought i was a along with the other mistakes on cert is a bit poor.
 
Last edited by a moderator:

Reply to ze testing - high current or no trip in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
795
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
827

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top