Am I correct in thinking that when doing a Ze test using a 1553, the dial needs to be set on the 'Hi' setting in the green loop section of the dial settings?
Cheers
Cheers
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Ze testing using a MFT 1553 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
If you want to conduct a high current test due to there being no RCD's upstream, then yes!
A Ze test is Live/dead test, ie you are working live, but all circuits in the installation are isolated due to the fact that you have the main protective conductor disconnected.
For this reason RCDs are not a consideration, and a high resolution test is performed.
Ok, next stupid question...
I thought a Ze test was carried out at the installation's main switch, under what circumstances am I likely to find a RCD between the main switch and the service head?
You may have an RCD protecting the tails depending on how they have been installed.
Nuisance tripping in that scenario would be putting it mildly
So I presume discrimination would need to be spot on.
Whys that then? Time delayed RCD
I merely mentioned the upstream RCD due to the fact that the "HI" loop setting should be used whenever possible, due to the higher current being able to show any latent faults in the connections, and also the fact that the accuracy of a high current test is much better.
If there is an RCD upstream of whatever you're testing, be it a submain or a final circuit, then a low current loop test should be applied, but in all other instances go for the high, you know it makes sense!