hi,i have tested ze on two installation both being tns.the results are 0.08 and 0.12.these figures seem very low for a tns system.are these normal or am i doing something wrong im using a kewtech kt64,,thanks
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Ze testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
one other point is are you testing ze or pfc ? with my fluke ze tests between line/earth and pfc between line/neutral, you will get a much lower reading of resistance when set to pfc.