Ze testing | on ElectriciansForums

Discuss Ze testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

W

waynelester

hi,i have tested ze on two installation both being tns.the results are 0.08 and 0.12.these figures seem very low for a tns system.are these normal or am i doing something wrong im using a kewtech kt64,,thanks
 
I have come across Ze values as low as that on a TNS before so I shouldn't worry too much. You are probably very close to the DNO sub.
 
only query is: are you disconnecting the main earth from the board before testing Ze to eliminate parallel paths?
 
one other point is are you testing ze or pfc ? with my fluke ze tests between line/earth and pfc between line/neutral, you will get a much lower reading of resistance when set to pfc.
 
one other point is are you testing ze or pfc ? with my fluke ze tests between line/earth and pfc between line/neutral, you will get a much lower reading of resistance when set to pfc.

Huh.

PFC.... Resistance???

Are you referring to likely reduced impedance between PFC and PSC?
 
Last edited:
if you like, The point i was makeing in relation the the op was that my fluke gives a Ohms reading when set to ze and pfc this is obviously measuring a differant fault path and if the op was not familure with testing and or his tester he may be confusing the 2.
 
sorry dont know what you mean, i have obtained two very low readings for ze on a tns system and was wondering if this was normal or was i testing incorrectly,also the pfc comes out at about 3.2ka which i supose is about right when calculating using ohm law
 

Reply to Ze testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
795
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
827

Similar threads

  • Question
The issue I was having turned out to be a faulty transformer on the pole 30m away... after hassling the northern powergrid (and having then visit...
Replies
9
Views
883
The actual listed observations seem easily resolvable, comfortably less than a day's work. The picture of the supply poses a few questions...
Replies
5
Views
999

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top