Had a bit of a problem today

I was carrying out a PIR in a car hire kiosk in an airport today. The small kiosk had it's own DB supplied via a SWA cable.

For recording the Ze on the test sheet I understand that this has to be carried out at the supply entry point but with working in an airport everything is 100 times more stringent than working most places, I was not permitted access to the main switch room.

So I measured the EFLI at the DB main switch 60947-3 which was 0.28 Ohms

Would it be satisfactory to record this value as the Ze or would I be better off putting L/M in the Ze box?
 
That's a surprisingly good reading.
Record this value as the Zdb, and put on your reports limitation to the true origin of the installation. You could ring the supply authorities, or maybe somewhere there, so that you can gain the information by enquiry..
 
Had a bit of a problem today

I was carrying out a PIR in a car hire kiosk in an airport today. The small kiosk had it's own DB supplied via a SWA cable.

For recording the Ze on the test sheet I understand that this has to be carried out at the supply entry point but with working in an airport everything is 100 times more stringent than working most places, I was not permitted access to the main switch room.

So I measured the EFLI at the DB main switch 60947-3 which was 0.28 Ohms

Would it be satisfactory to record this value as the Ze or would I be better off putting L/M in the Ze box?

Technically, this value is Zs or Zdb, as you say, there is only 1 Ze for an installation and I guarantee you that you will never get to isolate the installation and measure it!

I would put LIM in the Ze box and include the reasons in your 'extent and limitations' box ie. 'main supply characteristics not verified by client request'
 

Reply to Ze in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
798
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
828

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top