ze | on ElectriciansForums
ze
  • Thread starter chopperxbox
  • Start date
  • Replies 18
  • Views 2K
Discuss ze in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
C
chopperxbox
I need to do a ze reading on a pme system. What's the maximum allowed reading and is it still a three lead test as the earth comes through the neutral. Really appreciate any help. Not had to go this before. Thanks
max. is 0.35Ω, and it's a 2 lead test on hi-current. don't forget to dis. the earthing conductor for the test (after isolating the installation).
I am worried that someone has asked for the max reading before doing the test its the first thing that hits you as you open the OSG mind as long as they don't ask how to do it as well
sorry but im not near my osg and needed to know. thanks for the direct simple answer without all the trolling. really appreciate it telectrix. thanks again
Reply to ze in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
For what OCD? There may be other means of over current protection that allow a Zs of0.45 (HRC Fuse?)
FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!