Hi all. Just a quick one: are you allowed to run a cable (twin and earth) through the space under a bath tub, which still constitutes zone 1?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Zone 1 under bath tub in the Talk Electrician area at ElectriciansForums.net
Explain?Just make sure it's RCD protected to cover yourself.
Explain?
Well I'd cover it anyway just for peace of mind.
I thought under the bath was out of zones IF you could only access it with a tool? Screw the bath panel shut [emoji38]
It changed when the byb came out its now zone one all the time now
This statement does not match with the current wiring regulations requirements, the area under a bathtub is zone 1, however if cannot be accessed without using a tool then it is outside the zones.It changed when the byb came out its now zone one all the time now