Hi,
been a lurker on this forum for a long time, but this is my first post, doing some electriclal work which i will be using for my niceic assessment, need to run main protective bonding to the gas meter which is in a unit underneath the kitchen sink, the only way I can see is to chase in by the corner of the door and along the top of the skirting board into the unit, would this be ok as obviously it is not in a zone, just want to make sure as don't want to be tripped up come assessment time with Mr niceic.....
 
Ive got the 10mm earth from the cu under the stairs to the front of the house waiting to dropped down from upstairs into the kitchen, but there is no 'zone' as there is no sockets etc on that wall the only way I can see is to come into the kitchen in the corner and come down and across the top of the skirting board, the client doesnt want it to go outside,the only way I could think is to run it in a earthed metal conduit but it seems over the top as it isnt carrying current
 
I wouldn't worry too much about zones in this instance, as the bonding conductor is not a circuit.....be hard to RCD protect it etc.......I would do as already advised though and try to avoid any chasing, as is much easier
 
Into the room, along the top edge of the wall, and down the corner then under the cupboards.... if that is possible.

From what you've said you need to do some chasing so it would be good practice to do it in zones.
 
I wouldn't worry too much about zones in this instance, as the bonding conductor is not a circuit.....be hard to RCD protect it etc.......I would do as already advised though and try to avoid any chasing, as is much easier

Nobody seems to know about zones, and that includes some electricians:joker:

True, but it does ease the conscience if you had to be naughty......not that I would, well not usually.......:devilish:

Think I would say that you maybe one of those electricians that struggle with regards to CABLE and zoning.

As the OP stated it is a 10mm conductor I would assume it is a cable and as we know regulation 522.6.101 clearly states that a
cable concealed etc etc.

So it as nothing to do with it being a circuit or not, a cable buried is a cable buried and therefore needs to be afforded the protection required in the regulations.

Also if you want to read the regs an rcd is only one way to protect a CABLE there 4 others
 
OP - go back and look at the pictures in the OSG....where else is considered a zone?
 
Think I would say that you maybe one of those electricians that struggle with regards to CABLE and zoning.

As the OP stated it is a 10mm conductor I would assume it is a cable and as we know regulation 522.6.101 clearly states that a
cable concealed etc etc.

So it as nothing to do with it being a circuit or not, a cable buried is a cable buried and therefore needs to be afforded the protection required in the regulations.

Also if you want to read the regs an rcd is only one way to protect a CABLE there 4 others

Can't disagree there (as usual).

Oh, welcome back mate.
 

Reply to Zones for main protective bonding in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
838

Similar threads

Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K
  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top