Is it to be expected that a Zs test carried out using 3 leads (No Trip) will return a different result from one using 2 leads?

If so, can someone kindly explain what causes this.

Cheers
 
Also if your using 3 leads it's because there is a rcd you don't want to trip, the rcd changes the reading slightly to, try doing a ze either side of the rcd terminals and see what you get with your tester
 
Think you will find that the only difference between a 2 and 3 lead test meter is that the connection for the neutral to allow the meter to work is that on a 2 lead meter is made internally in the meter where a 3 lead it is not and you need to make a physical connection to the neutral.
 
Also if your using 3 leads it's because there is a rcd you don't want to trip, the rcd changes the reading slightly to, try doing a ze either side of the rcd terminals and see what you get with your tester

Well when I say 3 leads, what I was actually doing was using the Plug adapter on a socket, and switching between the Hi and No Trip settings. The circuit in question doesn't actually have an RCD protecting it. I was just wondering what was causing the differences in the readings.

Cheers
 
i have recently finished my 2392-10 course and have my 2391-10 course booked for the end of september. when undertaking r1 and r2 vaule on a ring circuit at my workplace all the sockets have fly leads and are all connected via steel from the back boxes in the sockets, is it possible to just measure l-l n-n e-e and divide by 4 instead of the figure of 8 method because it will take to much time to dissconnect all possible paralell paths?
 
as widdler says, noise can cause the difference. i find it's worse if you have radio 1 on. the best results are obtained when you tune your radio to classic FM.
 
i have recently finished my 2392-10 course and have my 2391-10 course booked for the end of september. when undertaking r1 and r2 vaule on a ring circuit at my workplace all the sockets have fly leads and are all connected via steel from the back boxes in the sockets, is it possible to just measure l-l n-n e-e and divide by 4 instead of the figure of 8 method because it will take to much time to dissconnect all possible paralell paths?

No . A
full test with cross connections must be done- otherwise you will not find if you have a ring within a ring
 
Well when I say 3 leads, what I was actually doing was using the Plug adapter on a socket, and switching between the Hi and No Trip settings. The circuit in question doesn't actually have an RCD protecting it. I was just wondering what was causing the differences in the readings.

Cheers

A test with two leads is using a higher current therefore is more accurate and because of that you should use when possible ( when you do not have additional rcd protection)
 
- by cross connecting at the board ( l-n...n-l) you also confirm polarity at each socket outlet,
- When you measure l-l , n-n, e-e, .....e-e will return different results as its a smaller csa ( usually 1.67 times the live conductiors value)

- cross connecting l-e , confirms the cpc is connected to each socket outlet

- also , in my tution of the 2391 ....we got hammered for calling it an earth....' its a cpc ( circuit protective conductor)



Hope im right, and it helps
 
Just to throw a spanner in the mix we were all told that you had to test a light circuit at the the ceiling rose or light point all of a sudden Megger bring out their 1700 series tester and say you can do it with a 2 lead set up at the switch and now they are in discussions with the registration companies to get an agreement
 

Reply to Zs.... 3 Lead Vs 2 Lead results in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
818
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
885

Similar threads

Having some issues with my companys fluke 1662/1663 tester. Zeroing 2 leads for continuity test we get the value 0.08 which is expected. The issue...
Replies
0
Views
264
The actual listed observations seem easily resolvable, comfortably less than a day's work. The picture of the supply poses a few questions...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top