hi all just a quick question about the above title,go easy with me if i am missing something obvious here lol, why do you have to put zs at d/b on the eicr(got a copy of part p doctor and on his sample of schedule of test results he as put the ze figure in there and then put ze in brackets at the side of it,if you was to do a zs test at d/b do you just do it at the main switch line in with switch open and then obviously to main cpc bar in d/b, obviously you could expect to get a lower reading than the ze because of parallel paths, and the next 1 Ipf at d/b wouldn't this just be the same as the pfc you put down on the first page of the eicr so why do you have to put it down twice cheers
 
Your ze may not be at the board, maybe a scenario like fused isolator then to consumer unit, your ze would be at fused isolator and then you would have a db zs at the consumer unit
 
The reason why Zs is now required to be recorded on the schedule, is because recording a value that has already been recorded, is pointless.
Zs is very likely to be different from Ze.
Also this now allows the schedule to be used where there are multiple Dbs without having to alter the Ze to Zs.
 

Reply to zs and Ipf at d/b on schedule of test results in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
330
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
855
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
975

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K
I'm not sure on the environmental implications, a good quality integrated fitting will last many years and be more energy efficient than the GU10...
    • Like
Replies
13
Views
1K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top