just a few pointers on this please, been to a property today where a large shed is supplied by a 3 phase genny. Inside the shed are numerous sockets, motors for opening large doors and lights. Started to do a Zs test on sockets, (ring main circuit) supplied by 32a mcb, within seconds RCD would trip off. Tried a few different sockets all with the same result.
Checked and double checked tester, no trip setting etc and still tripping RCD.
Did an RCD test on sockets, 1/2 times, 1 times etc. all times were over range :confused: am i doing something wrong :eek: no other tests were done as had to get away but if anyone has any pointers they would be much appreciated
 
continuity and IR on dead circuit/s first. you could have a small leakage which is adding to your no=trip test current
 
Normal installation testing on generators can throw up some strange things...came up against this many years ago..using far older test equipment....was unable to take any Zs readings on an installation powered by three phase genny...it turned out that as I initiated the test the generator sensed the increase in load (basically introducing small earth fault with tester) and upped the voltage to overcome the dip??????Mentioned it to a guru of electrical lecturing who explained it all to me but far too boring to comprehend....needless to say testing on generated supplies can be strange. The other thing I did remember was the question of can the generator supply the required fault current required to trip protection in required time....before genny blows up or something?????
Anyway...will get back to my Cad....good luck with the testing mate!!!
 
Are you sure it's TT - I don't have much experience with generators, but I was under the impression they tended to be TN-S
 

Reply to Zs and RCD testing on 3 phase generator supply in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
790
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
813

Similar threads

As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
Replies
20
Views
2K
L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
654

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top