Goody

-
Joined
Jan 21, 2010
Messages
638
Reaction score
94
Location
London
I have been testing a ring circuit with two FCU’s, one of which feeds a cooker hood & another a oven light and gas igniters. Found R1+rR2 and R1+Rn on all the sockets including the FCU’s and Zs on all the sockets using Fluke with 3 pin cable set.

As the cables to the hood & the gas cooker are concealed under tiles and their ends are not accessible (going into sealed connectors), will R1+R2 readings at the FCU’s suffice? What am I going to write on the EIC for these?

Again, for Zs at the FCU’s, can I use hypothetical values {Zs=Ze+(R1+R2)} or should I actually measure them at these points? Also how do I NULL (zero) the 3 pin cable set prior to measuring Zs at the sockets?

Thanks in advance!
 
you should measure the Zs's, and you don't null the leads for Zs. only null for R1+R2 ( continuity ). measured at the FCu's is fine IMO.
 
Depends what you are testing for. Normally the FSU results will be where you end, same question on an immersion heater in another post. The EIC will record the values at the FSU. As long as you note that you have calculated Zs on the EIC it is ok IMO. since generally the measures Zs will be lower than the calculated Ze + (R1 + R2) due to parallel earths.
 
If the Zs is going to be lower, with the parallel paths, then the fault current will higher, so attention needs to be on whether the MCB is capable of handling the breaking capacity. A direct measurement is always best.
 
If the Zs is going to be lower, with the parallel paths, then the fault current will higher, so attention needs to be on whether the MCB is capable of handling the breaking capacity. A direct measurement is always best.

No, that's why PFC is measured at the point at which the protective device is required to break the fault current, not at the extremity of a circuit where Zs should be measured.
 
The regs say you need to measure R1+R2 612.2.1 and that Zs needs to be measured 612.8.1 in order to proove compliance with 411, TN requirements. So there you have the regs view.
 
From GN3 page 95:
"*12 Earth fault loop impedance Zs
This may be determined either by direct measurement at the furthest point of a live circuit or by adding (R1 + R2) column 6 to Ze. Ze is determined by measurement at the origin of the installation or preferably the value declared by the supply company used.
Zs = Ze + (R1 + R2). Zs should be less than the values given in appendix 2 of the On-Site Guide or Appendix 2 of GN3."
 
The regs say you need to measure R1+R2 612.2.1 and that Zs needs to be measured 612.8.1 in order to proove compliance with 411, TN requirements. So there you have the regs view.

Absolutely not, there is no requirement in BS7671:2008 to measure R1+R2, the requirement is to prove continuity of the protective conductor-this can be done with a bell/buzzer set as long as it meets the requirements of 612.2.1 regarding output voltage and short circuit current.
 
Strictly speaking the regs say.
612.2.1 "a continuity test shall be made..."
and 612.8 a) "measurement of earth fault loop impedance (see 612.9)
and 612.9 "...the relevant impedances shall be measured, or determined by an alternative method."

Ok so my paraphrasing not quite what some were expecting.
The key things being proof of conductor (include cpc) continuity and a verification that Zs is less than or equal to the allowed value, be this by measurement or "an alternative method".

I hope this keeps all happier.
 

Reply to Zs at the FCU’s – advice needed, please! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
810
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top