ZS before RCD? | on ElectriciansForums

Discuss ZS before RCD? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

J

jamminuk

Hi,

I've looked for the answer to this question on her ebut couldn't find it. Can anyone tell me why it's important to do a ZS test before an RCD test?

Thanks

Ben
 
your Zs test proves that you have continuity between line and cpc. this should be established before RCD testing. though i am unsure if a high Zs reading would have an effect on the RCD test as such.
 
The Zs reading is done first to ensure that you have a sufficiently low resistance earth fault path. If the Zs is too high, then it is possible that insufficient current would flow down the fault path to trip the RCD. In the event of a "real" fault then there may well be current flow other than down the fault path (ie through you to earth via another route(s)) so the imbalance between line/neutral would/should still cause a trip. However you need to ensure that the route you are using when testing the RCD timing is good. Hence the Zs before RCD tests.
 
RCD test can last for 2 seconds, if you do not have a good earth the voltage of the earth circuit and any metal attached to it can raise to 230V for the duration of the test.
Hence it is essential to test for a good earth before an RCD test.
 

Reply to ZS before RCD? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

Similar threads

Did a fuseboard change yesterday from an old wylex board to dual rcd on a TT system with 14ohms ZE and finished pretty late. Went back this...
Replies
0
Views
490
  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
685

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top