Did a Periodic today on a TT system. The Ze was a reasonably healthy 38 Ohms and the Ze figures for the various circuits were around the 25 ohms figure. All circuits are protected by a 30mA RCD and the boards main switch is a 100mA time delayed RCD. The Zs figures are way higher than the recommended figures on Pg 103 OSG but am I right in thinking that they comply with 7671 when I look at the table 41.5.

Sorry to ramble on and thanks in advance
 
Yup, Zs results for a TT system will always be higher than what is allowed when using an MCB/fuse for ADS, hence why the need for RCD protection on the final circuits. There is a calculation for RCD requirements at the front end, but if everthing is protected at 30mA and your Zs are relatively low, then there shouldn't be a problem. Have a look at 411.5.3 for guidance.... :)
 
Last edited:
Hi.

As it's a TT system then yes it's table 41.5 you need to refer too.

Basically for a 30mA the max permitted Zs in order to achieve disconnection before the safe touch voltage of 50V is exceeded is 1667ohms. For a 100mA it's 500ohms.

The Ze (Ra) should be no more than 200ohms but as you have 38 then jobs a good un.:)
 

Reply to Zs figures for a TT System in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
290
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
276
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
354

Similar threads

  • Question
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
Replies
10
Views
2K
OLDBOY
O
  • Question
Good point, I was assuming an up-front RCD is for fault protection within DB, etc, and to cover for a failed RCBO for fault conditions, not as...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top