hi all, been doing some testing today on the new lighting circuit and sockets i have put in the garage for my first assesment, everything tests ok my lighting circuit(6A mcb) R1 +R2 is 0.59, and the sockets(radial on 20A mcb) R1 + R2 is 0.28, my ze at origin is 0.14 so calculation of zs for each circuit would be roughly 0.73 for lights and 0.42 for sockets, i use the megger mft1552 which i have to do the zs test on no trip 3 lead test(dual rcd board) i know the reading on the actual test are going to be different to my calculations slightly, they come back at lights 0.83 and sockets 0.52 both circuits are 0.10 higher on the actual test probably because of the impedance in the rcd,s, everything still well within the limits so no probs, what would you advise to put on the cert the calculation or the actual test results, only asking as when the assesor looks at the cert's ze and R1 + R2 and i have put the test figure's in would he understand that they are 0.10 different because i have had to do it on no trip loop because of rcd,s read alot of thing on net saying put the actual test figure's in then lots say just calculate it cheers