Hi all,

Domestic property rewire.

Kitchen ring measured Zs of 14.6

checked the Ze and way up at 580.


Banged in an earth spike, Ze now down to 160

Checked Zs at same socket outlet and it measured 80.5

???

Why would this occur?

Just got home not had time to think cleary, any pointers please.

Kitchen ring
r1 = 035
rn= 0.34
r2 = .54

The installation looked like TN-S at first glance, a ribbon earth from MET clamped to incoming supply cable?
Thank you
 
Last edited by a moderator:

Reply to Zs increase after lowering Ze? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top