Mark2009

Hi
Done a zs on lights today got reading 1.28 tried again but the meter kept tripping Kewtect Meter, how can i use maths to get the answer.

Thanks

Mark
 
Zs=Ze + R1+R2 ,, but whats wrong with a reading of 1.28 if its on a 60898 MCB then the max is 7.66
 
Last edited by a moderator:
Hi
First i would like to say that if everyone is so bright why are they on this fourm, i asked a simple question, Kewtect are not the best meters and i know i can bridge the RCD so it wont trip i just wanted the easy option. Kama could hit any of you at any time.
 
dont think there was any mention of the RCD tripping in your post you said meter , the calculation is standard practice , we will never stop learning , but if you had explained your question a little clearer then the guys could have given you the answer that you required ,and we did
 
Last edited by a moderator:
Hi
Done a zs on lights today got reading 1.28 tried again but the meter kept tripping Kewtect Meter, how can i use maths to get the answer.

Thanks

Mark

If you had worded it : when i carry out a Zs test on a lighting circuit , the RCD keeps tripping how can i calculate the Zs

im not having a go mate but
 
Mark I apologise for my comment. I'm in a bad mood through a bad afternoon and took it out on you. I'm sorry mate, I don't know you nor your compentency so I don't feel I had a right also I've been there before and not too long ago asking questions like that. No hard feelings. :)
 
Hi
First i would like to say that if everyone is so bright why are they on this fourm,

Well that's obvious. I'm here to share my excellence with the rest of you and to give you all half a chance.

i asked a simple question,

Too simple. It was the equivalent of a cruise liner captain asking which side was starboard to a passengers Chihuahua, something you should really already know.

If you are going to equip yourself with an installation tester, you need to learn how to use it. How can you correctly complete any installation or periodic report with knowing how to obtain Zs values.


Kewtect are not the best meters and i know i can bridge the RCD so it wont trip i just wanted the easy option. Kama could hit any of you at any time.

Well I disagree with you there as well also..





.. sigh
 
Hi
Done a zs on lights today got reading 1.28 tried again but the meter kept tripping Kewtect Meter, how can i use maths to get the answer.

Thanks

Mark

Cant see why you want to retake the Zs
You have a reading of 1.28 Use that reading for your Zs unless you suspect the meter is dodgy (you wont then have to use maths for the answer :))


Does your particular meter normally have the facility for non trip and the non trip is not functioning ?
 
AS your circuit is also RCD protected then the ZS will be 1667 which makes the 1.28 you have no longer relevant.
 
just wondering no expert myself but isnt <ZS=ZE+(R1+R2)> better to find the zs in the first place as if your useing a loop impedance tester will be less then <ZS=ZE+(R1+R2)> due to parallel paths?
 
Come on boys and girls, the bloke asked a question, either answer it or ignore it, this forum is too good and professional for crap like this. The big shed forum is the place for moronic comments and replies.

Cheers...........Howard
 
Hi
Done a zs on lights today got reading 1.28 tried again but the meter kept tripping Kewtect Meter, how can i use maths to get the answer.

Thanks

Mark

if ur gunna try and use math to figure it out ur gunna be there a long time get ZE from the board and add your R1+R2 from your previous tests.
 
Come on boys and girls, the bloke asked a question, either answer it or ignore it, this forum is too good and professional for crap like this. The big shed forum is the place for moronic comments and replies.

Cheers...........Howard
I am with you on this one sirkit breaker
 
I am with you on this one sirkit breaker

You and SirKit need to look beyond a simple post and at the severity of people using equipment when they cannot display the competence to use it effectively.

It's dangerous, pure and simple.
 
You and SirKit need to look beyond a simple post and at the severity of people using equipment when they cannot display the competence to use it effectively.

It's dangerous, pure and simple.

I have to agree with Widdler!! Lets not forget we are here to help and advise, and to be professional but remember guys Zs is a Live test, in a cramped ceiling rose or switch!

Could be a recipie for a small disaster if the OP is unsure
 
just wondering no expert myself but isnt <ZS=ZE+(R1+R2)> better to find the zs in the first place as if your useing a loop impedance tester will be less then <ZS=ZE+(R1+R2)> due to parallel paths?

Cant get better than a live Zs reading in my opinion, the parallel paths won't go away or segregate just before the event of a fault.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
ZS Lighting
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
31

Thread Tags

Advert

Thread statistics

Created
Mark2009,
Last reply from
nickblake,
Replies
31
Views
3,593

Advert

Back
Top