scott g
http://www.------.org/forums/forum/i/icons/arrow.gif Or do you use a calculated Zs instead
i rekon if the r1r2 plus the ze taken at the board is lower than the accepted values for zs then this is a better result to show as it is worst case scenario, it doesnt take into account parallel earths so a live test will always be lower, so if a dead test passes then a live test should do too.
I like to do Zs just to confirm my initial confirmation. It takes 5 seconds to do so why not. I too record the highest value, usualy r1 + r2 +Ze.
well it does prove that the neutral is there, but when testing lights it becomes akward to get all 3 leads in place, i know there are all sorts of wonderful toys to make this easier but i supose its down to personal preferance :)
Only circuit your permitted to do zs reading if you have socket interface is ring/radial socket outlets all other circuits must be cal.
Hey all.
I think the whole "do you measure or calculate Zs" thing has been threaded to death now.
But in answer to your question I always measure Zs and like to compare it with the calculated value to make sure that all is as it should be.
Cheers.
If live testing is not allowed how do you get a Ze reading at the board :confused:
Reply to Zs live Testing - does everyone do it? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Unless the circuit is new or has recently been tested/certified by a.n.other, I'm not sure how you prove the circuit is 'safe' to connect to...
Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...