I am testing my dads house to get a bit of practice and I dont understand the readings?

Its a TT with an Ra of 39ohms, yet when I use the MFT to do a Zs on the sockets I get anywhere from 0.21 - 1.09ohms. I dont understand how this can be lower than the Ra, I must be doing something wrong?

Thankyou.
 
TT systems can give fluctuating readings.. Check Ze is stable before, during and after testing circuits.

Meter leads may be faulty did you short test them a few times.

Contact terminals you are testing at may be resistive due to anti-corrosion film on them try down to clean copper...

Parallel paths ... you have reconnected the bonding and reduced the Ze as mentioned above.



Quite a few reasons really but a few to head you in the right direction
 
Or.... Your water service pipe is inextricably linked (as in joined) to your neighbours, and they have a TN earthing system that is bonded to the water pipe.

seen it a few times.

Ra 17.8.... Zs at the socket 0.34!?!?! How can this be"..................:hammer:
 
I did leave the bonding in place when I did the Zs. Would that bring the Zs down so much? Ra was 39.. Zs was say 1ohm which means the gas and water pipes have made it drop by around 38ohm.. how can they do that? Thjats means they are better than the rod!!??
 
I did leave the bonding in place when I did the Zs. Would that bring the Zs down so much? Ra was 39.. Zs was say 1ohm which means the gas and water pipes have made it drop by around 38ohm.. how can they do that? Thjats means they are better than the rod!!??
so what is your question again, I thought we gave you some Ideas which will get you going in regard to understanding what may be the reason why the reading is so much better than the rod alone? as for being better, you cannot have water or gas pipes as a main earth, you know what your main reading is, you said 39 ohms, thats pretty good, why don't you try to test the readings to the pipes lol, give yourself some more practice.
 
As has been said, water and gas supplies can often give you a much better/lower resistance than a rod, but you are not permitted to use these supplies as your main earth.
 
That all makes sense now, sorry for sounding a bit dumb. My head just thought 'main earth' must be better than pipes as thats what its for!
 
That all makes sense now, sorry for sounding a bit dumb. My head just thought 'main earth' must be better than pipes as thats what its for!

All part of the learning process, ask the question and think about the responses ...... parallel paths in there somewhere!!
 
Might be time to ask the DNO if PME is available in your parents area, and if it is, making use of that facility. Is the house supply via an overhead system, if so there's a good chance that the overhead supply has been PME'd. Check the poles, should be a N-E bonding cable to a rod every third or 4th pole... Along with metal/taffo PME warning signage....
 

Reply to Zs lower than Ze???? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
701
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
751
so Ze 0.35Ohms and my Part of the Circuit just half of R1+R2 is 0.19353Ohms as its 1.5mm x 10m so well under but dont know of any switch gear...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top