Can anyone help...

I'm trying to get the Zs reading on a radial lighting circuit but my Megger MT1552 keeps tripping (TRP) during the test.

I'm: Performing a Live test Main switch, RCD and MCB Closed

and performing the test at various points on the circuit including the furthest point using the 3 lead test method set to the 'no trip' loop impedence setting results in the Megger tripping. I've also tried only using two leads with the same result and also the normal loop impedence test resulting in the RCD tripping as expected.

Incidentally I tested the Zs of a ring circuit using the socket attachment without problems and with results matching calculations.

Any help would be appreciated as to why my Megger is tripping.
:(

Thanks
 
I understand the calculation concept but you shouldnt just use the calculated method alone. It should be substantiated with a measurment from the EFLI tester.

Any ideas for why it's tripping???

:)
 
If it is a B type breaker it will do it 9 out of 10 times (i have given up trying) as others say do calc .if you

really want to do test put a D type in and test then put B type back in,this seems a bit of a waste of

time to me though as if you have done ZE and r1 and r2 you have already done main tests.

If you are worryed there is nothing wrong with your tester.:)
 
As above really.

You will probably find that swapping the MCB for even a B16 or similar may also help.

just make sure to swap it back to the 6 when done.
 
Forgot to mention I'm using a 10A MCB Type B for lighting due to load and the property's original wiring.

Thanks for all your suggestions already. Any more will be very welcome.

I'd just like to say that this site is really useful.

Thanks electricians forum... and members :)
 
I once said swap to to 16a to test and swap back to 6a in a testing course .

The instructor looked at me as though i had slept with his wife and said no way.

we live in the real world though:)
 
Hi Big Man. If your not already use the clips to take the reading not the probes. And yes its a 3 lead test on no trip for the megger. The smallest of movement with the probes will trip the RCD.
 
Good advice, thanks I'll take that on board. But its not so much the RCD tripping as the Megger internally tripping whilst attempting to gain the reading.

Any ideas? Is it a design fault or have I done something wrong?

:-/
 
It comes up with TRP on the screen. I assumed it is a safty feature or prevents the RCD from tripping so you don't have to run off to the consumer unit. Either way I don't get a reading.
 
I've used the 1552 before and i got this when either one of my connections wasn't firm enough, or if the leads weren't pushed home in the tester or the croc clips.

Maybe your testers developed a loose connection have you dropped it?
 
Last edited:
U'll also get the trip msg if you move the probes. I had the same problem. Try using all 3 clips and make sure u have a good connection on the earth clip.
 
Big Man. I had the same prob. Have you got new leads, changed them recently? If they're fused leads, check the rating of the fuses, they should be 10A for the 1552. For me, it was a case of RS giving me 0.5A fuses for my leads and I didn't notice before I put them in. It had me baffled for a while. :rolleyes:.
 

Reply to Zs & Megger MT1552 Tripping in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
740

Similar threads

Having some issues with my companys fluke 1662/1663 tester. Zeroing 2 leads for continuity test we get the value 0.08 which is expected. The issue...
Replies
0
Views
252
KT66EVA (KT66DL & KEWEVA) - ÂŁ1073.60 + VAT if you shop about as a combo
Replies
5
Views
611

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top