Wilson12

-
Trainee
Joined
Nov 15, 2015
Messages
133
Reaction score
3
Location
London
If the maximum zs is okay up until 1667 ohms protected by a rcd why do we care about maximum disconnection times for the mcbs e.g why do we test and it's important to meet 1.37 or 1.1 zs on a 32 amp circuit
 
The 80% factor is a good estimate of copper resistance at 70C when remeasured at 20C. So it's not a tolerance.
The BS7671 tabulated values will have the conductor temperature stated, and it's often 70C. We tend to test and measure when a circuit is at room temperature and so we multiply by 0.8 to get an equivalent value.
 
Upvote 0
The 80% factor is a good estimate of copper resistance at 70C when remeasured at 20C. So it's not a tolerance.
The BS7671 tabulated values will have the conductor temperature stated, and it's often 70C. We tend to test and measure when a circuit is at room temperature and so we multiply by 0.8 to get an equivalent value.
I think I have probably misinterpreted your words, but the proximity of the 80% appears to refer to correcting a measured resistance to a 70°C resistance.
Whereas it is the 70°C resistance that is multiplied by 0.8 to give an value close to the expected measured resistance at 20°C.
Or alternatively the resistance measured at 20°C is multiplied by 1.2 to give the expected resistance at 70°C
 
Upvote 0

Reply to Zs ohms with maximum rcd ohms in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
282
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
780
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
792

Similar threads

As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
Replies
20
Views
2K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
947

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top